Do I need to take special consideration for ground and neutral connections on the secondary of a Electrostatic Shield Isolation Transformer? Its a delta-wye 480 - 208/120. I've heard that you bond the neutral and ground at the transformer...if so...How do I deal downstream with grounding the panel frame without creating a parrallel return path? Many thanks for any help....reference to a wiring diagram would be great!

Thanks folks!

Sense
 
Ground the transformer like any other. One neutral to ground bond, either at the transformer or at the panel. With only one neutral-ground connection, there are no parallel return paths.

The shield is typically bonded to the transformer frame.
 