- Jul 8, 2009
- 17
Hi all,
My question is a bit wide, and I apologize for that.
Often, Electrostatic ground shield are used in Rectifier transformer, I manage to get the following explanation from :
Electric power transformer engineering / edited by James H. Harlow. // ISBN 0-8493-1704-5
Ok for the second part about high-frequency disturbance from the rectifying process.
But I dont get why ungrounded secondaries systems are more vurnerable to disturbance (from primary) than grounded systems.
Could anyone clarify it for me?
Thank you in advance.
My question is a bit wide, and I apologize for that.
Often, Electrostatic ground shield are used in Rectifier transformer, I manage to get the following explanation from :
Electric power transformer engineering / edited by James H. Harlow. // ISBN 0-8493-1704-5
Electric power transformer engineering said:"2.4.13 Electrostatic Ground Shield
It is usually desirable to have an electrostatic ground shield between the primary and secondary windings.
The electrostatic ground shield provides capacitive decoupling of the primary and secondary windings.
Generally, the winding connected to the rectifier circuit is ungrounded. Without the presence of the
electrostatic ground shield, transients on the primary side transfer to the secondary side of the transformer.
These may be approximately 50% of the magnitude of the primary transient if there are no
grounds in the system. This is high enough to fail secondary windings and core insulation or to cause
rectifier-circuit failures. The other normally considered advantage to the system is the minimization of
high-frequency disturbances to the primary system due to the rectifier second part."
Ok for the second part about high-frequency disturbance from the rectifying process.
But I dont get why ungrounded secondaries systems are more vurnerable to disturbance (from primary) than grounded systems.
Could anyone clarify it for me?
Thank you in advance.