Dear Mr. NickParker (Electrical)(OP)8 Sep 22 13:57
"...Is it okay to use Electrical control cables for PTC sensor wirs (from Field to MCC) which is to be laid along with Low voltage power cables. ? "
1. I noticed that two days had passed but there was no response.
2. I tried to answer it, for your consideration:
A PTC sensor operation/characteristic is based on the resistance.. When "cool", the resistance maintained at low ohmic value but sudden huge increase in ohmic value at certain "hot" temperature, (e.g. cool within say <100 Ohm to few kOhm when hot).
3. Its characteristic is independent of the Voltage, (4-20mA) current or induction of hi-frequency.
4. The sensor wire need on screening. However, as it is to be laid along with LV power cables, it shall have the same insulation voltage rating as the power cables.
Che Kuan Yau (Singapore)