Suppose you have a wide flange beam with joists framing into it, bearing on the top flange at 4'-0" o.c. and the beam has a compressive axial load. For the purpose of this question ignore any dead load, live load, self-weight, etc. The only load is the axial load on the beam.
Would you say that beam effective length is 4'-0" in the weak axis for the axial load?
From my point of view: the joists only brace the top flange so to say the effective length is only 4'-0" is incorrect. My thinking is that the k factor would be something similar to the k factor for plate buckling. A simple span plate with a simple support on one edge and free on the other edge (k = 0.425 I believe).
Would you say that beam effective length is 4'-0" in the weak axis for the axial load?
From my point of view: the joists only brace the top flange so to say the effective length is only 4'-0" is incorrect. My thinking is that the k factor would be something similar to the k factor for plate buckling. A simple span plate with a simple support on one edge and free on the other edge (k = 0.425 I believe).