Effect of higher frequencies on breaker and CT

Status
Not open for further replies.

pukar12345

Electrical
Mar 28, 2010
27
Hi All,

I have a feeder feed by Variable Frequency Drive (VFD)of 60-200HZ.
I have breaker and CT after VFD. Is there any effect on CT and breaker when frequency changes from 60 to 200hZ.
 
Replies continue below

Recommended for you

Don't do that. Just rely on the protections of the VFD. Most relays won't work above 75Hz, if even that high. The VFD will do a perfectly goo job. Breaker after the VFD is just asking to fry the VFD.
 
CT performance improves with frequency up to a certain point. Normally that's around the 30th harmonic or so.
 