Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

EF Cable Detail

Status
Not open for further replies.

Lutfi

Structural
Oct 20, 2002
1,036
Good morning to all. The attached detail was sent to me by the mechanical engineer on one of the projects that is under construction. The fan was approved and installed for lower wind speed than is required by code. The fan supplier is suggesting adding the four cables so that it meets the required wind speed.

Regards,
Lutfi
 
Replies continue below

Recommended for you

would the steel decking handle the load, I would make them weld a angle between joists/beams, and anchor to that. Provide you the loads so you can check uplift, bending in the angle.
 
That looks like the support for the cable at the deck would just rotate at the bottom. I don't think I like that.
 
Thanks for the input. I do not like the detail for the same reason UcfSE stated. I asked them to change the detail by welding the vertical pipe to larger base pate and then fasten it to the deck.

Regards,
Lutfi
 
Did the fan supplier or ME provide any calcs showing the reactions? I would expect the cables to be attached higher.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor