Eccentricity in an isolated footing

Status
Not open for further replies.

Buleeek

Structural
Sep 5, 2017
98
Hello,

I have an isolated footing and need to calculate maximum soil bearing pressure. The footing has a column offset as shown in the attached picture. In addition there is a moment. My question is, what "e" should I take into consideration? Should I just combine "e" from M/P and "e" from column offset?

And then, what is the formula for qmax assuming that e > B/6 (see attached)?

Please advise. Thank you
 
 https://files.engineering.com/getfile.aspx?folder=041ca01c-e7dc-4a67-9298-97b8799f20cd&file=IMG_2604.JPG
Replies continue below

Recommended for you

phamENG,

Thank you, that is very interesting. However that chart/method has a limitation that forces occur at center of the footing. I am looking for a solution where column is located off-center and moment is applied to it.
Thank you,
 
Sorry about that. I'd look at it as concentric with a moment to resolve the e from the offset, and then combine it with the other moment.
 
See below. Your 0.5' dimension is off scale, but the effective eccentricity is 1.1' which exceeds B/6, so most of the footing will have zero pressure on it.

Usually the load on a column has a maximum and a minimum value. You show only one load, 5000#. If the minimum load is less than 5000#, the effective footing width will be even less than 2.1'.

image_y1guvc.png


BA
 
BA,
Thank you for explaining this. It makes sense. If the moment was in other direction I would subtract one from another.
 
Buleek said:
If the moment was in other direction I would subtract one from another.

Yes, the net eccentricity would be e = 0.1' if the moment was reversed. That would make the entire 5'x5' footing effective and the soil pressure would be close to 200 psf throughout.

BA
 
BA,

According to my calculation the length of "active" part of footing is 4.2, not 2.1' as you pointed out. Please advise.
 
4.2 sounds accurate

**Assuming a weightless footing or your loads already account for the footing weight**
Sum Moments about bottom left (clockwise positive) = 5000 (2.0 ft) - 3000 ft-lbs = 7,000 ft-lbs
statically equivalent system puts your 5000 lbs force at 7000/5000= 1.4 ft from the bottom left of the ftg.

Limit of the Kern zone is 5ft/6 = 0.833 ft from the footing center or 1.67 ft from the left edge, so you are outside the kern.

Bearing pressure total load = [1/2 * B' * Q,max] * L
For static moment equilibrium the resultant of the bearing pressure needs to align with the static equivalent location of P:
centroid of a triangle is 1/3*base from the tall end
1/3 * B' = 1.4 --> B' = 3*1.4 = 4.2 ft = bearing length

From sum of vertical forces = 0, P = [1/2 * B' * Q,max] * L
5000 = 1/2 * 4.2 * Q,max * L --> 5000 = 10.5 Q,max --> Q,max = 476.19 psf

My Personal Open Source Structural Applications:

Open Source Structural GitHub Group:
 
Buleek said:
According to my calculation the length of "active" part of footing is 4.2, not 2.1' as you pointed out. Please advise.

You are absolutely correct! Looks like I was asleep when I responded before.

image_jcphoi.png