I'm a bit confused with touch potentials for a 1500kVA Transformer. Just switched industry so learning from scratch again.
Please reference the attachment (Powerpoint)
I've used a program to calculate the touch and step potentials of an earth grid I created under a 1500KVA Transformer.
Grid resistance = 1.25 ohms
fault current = 1913 Amps
On the first slide (touch voltages), the white area (8x6m around the transformer) shows safe touch potentials (<254.18V)
This is all good if i am touching the transformer under a fault condition.
However the Switchroom (MCC) is 3metres away from the transformer (just outside of the earth grid) and is in the unsafe touch potential zones (>254.18V). Does this mean that if i am touching the Switchroom under a fault condition, than it's unsafe? or is it OK and why? Someone asked me why we don't have an earth grid underneath the switchroom and i'm unsure of the answer.
Also, i would be expecting the touch potentials to lessen as you move away from the transformer, but the results show the touch potentials getting greater as you move away from the transformer.
Thanks for your help guys, looking forward to being enlightened!
I'm a bit confused with touch potentials for a 1500kVA Transformer. Just switched industry so learning from scratch again.
Please reference the attachment (Powerpoint)
I've used a program to calculate the touch and step potentials of an earth grid I created under a 1500KVA Transformer.
Grid resistance = 1.25 ohms
fault current = 1913 Amps
On the first slide (touch voltages), the white area (8x6m around the transformer) shows safe touch potentials (<254.18V)
This is all good if i am touching the transformer under a fault condition.
However the Switchroom (MCC) is 3metres away from the transformer (just outside of the earth grid) and is in the unsafe touch potential zones (>254.18V). Does this mean that if i am touching the Switchroom under a fault condition, than it's unsafe? or is it OK and why? Someone asked me why we don't have an earth grid underneath the switchroom and i'm unsure of the answer.
Also, i would be expecting the touch potentials to lessen as you move away from the transformer, but the results show the touch potentials getting greater as you move away from the transformer.
Thanks for your help guys, looking forward to being enlightened!