EddyWirbelstrom
A Dyn transformer with solidly earthed star point supplies an induction motor with either delta or unearthed star windings.
Attached Fig. 1 shows PTW32 Ver 9014 Comprehensive results for an earth fault on BUS_0003 with earth fault current contribution from both transformer and motor as expected.
Motor connection could be either star with unearthed star point or delta.
Included is the Comprehensive Short-Circuit text report showing current distribution.
Attached 2 below shows a three-line current distribution for an earth fault on BUS_0003.
Highlighted are the current distribution paths.
Current distribution on the transformer star side and motor is as expected.
PTW does not calculate current circulating in the transformer delta winding.
Using equal ampere-turns in primary and secondary windings I could not calculate the current circulating in the delta windings !
What is the current distribution in the delta windings ?