On rural (resource) access roads in our local it is common to install pipe pile foundations for small simply supported structures (12m-21m) with a dynamic equation such as Engineering News (ENR). We are dealing mainly with cohesive soils and friction piles; the use of dynamic equations has lead to some very conservative designs. I'm advocating the use of a PDA at a minimum, but they can be hard to find in a remote location. Unfortunately re-striking is not a common practice, as the time suggested for set up (3-4 days) does not fit into the construction schedule (5-8 days for structure installation).
Any comments on the use of dynamic equations to predict the capacity of friction piles?
I've noted that the FHWA is advocating a modified Gates and Washington State has adopted their own dynamic equations, what has been the experience to date with these systems?