In NYC it calls for a two hour rating wiht fire /smoke damper. Also check to see if you need to install plastic breakaway nuts and bolts in the event the duct separates from the damper assembly, the force will not pull the fire damper out of position. Dampers must meet fire smoke ratings as per local juristiction, in the healthcare setting, it must also meet State DOH code specifications.
You must also have duct smoke detectors in certain locations.