Duct material for Sulfuric Acid environment

Status
Not open for further replies.

Clymber

Mechanical
Jan 7, 2003
46
I am designing an exhaust system for a small room (~400SF) containing a closed, dilute sulfuric acid system. Airflow is approx. 6 ACH. Is galvanized (w/high-performance paint) the cheapest option, or would a plastic duct be more chemically resistant?
 
Replies continue below

Recommended for you

Plastic or fiberglass would be best. It is only a question of time before paint fails.
 
When you do this, check where the exhaust ends up.
I had a very unpleasant time recently, changing out galvanised equipment pad covers, for stainless on the roof of a facility, because the acid fumes had rotted the galvanising off the covers, allowing them to rust and get holes.
B.E.
 
Thanks. Looks like I'd better go with FRP for the ductwork AND the outlet louver.

-Brad
 
if you choose metal over frp, I would look at 316 LC SS, why not ask on the corrosion forums?

Take the "V" out of HVAC and you are left with a HAC(k) job.
 