Hello Everyone,

My question is when calculating drift for steel portal frame steel structure, does the Ridge/Apex level need to be checked also or is it only at Levels with diaphragms?

Thank you
 
Replies continue below

Recommended for you

Generally you check story levels....or whatever could hit an adjacent structure. A ridge is not something I'd check without a reason.
 
We use various drift limits (for wind) such as H/300, H/400, and H/500 depending on the type of exterior cladding - and use the levels at the floor diaphragms.
Have never used H (height) as to the top of the ridge of a sloped roof....perhaps to the mean roof height but not the ridge.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
I spoke to a couple local engineers, they had different responses. See image below for frame cross section. I was told that the drift would have to be calculated at ridge level because it’s a flexible diaphragm, and another said it’s not necessary.
 
 https://files.engineering.com/getfile.aspx?folder=80a64755-d4f3-4622-8d55-4e6b5e385a3f&file=072BBEAB-2E5E-467E-830A-53BFE010E93A.jpeg
WARose said:
A ridge is not something I'd check without a reason.
Here's a potential reason - Do you have deferred submittal/delegated design for non-structural framing? Will they need to isolate interior framing for drift and will there be any framing to the ridge/deflections large enough for you to be concerned? Perhaps a non-issue, but maybe worth a minute of consideration.

Judgement-In-Training
 
Here's a potential reason - Do you have deferred submittal/delegated design for non-structural framing?

Typically the answer to that is: no. But even if I didn't, I've never run across a situation like you mentioned (assuming I understand what you mean) where that would control.
 
Thanks, I would definitely have a look at the design for none structural members.

Another question as it pertains to a portal frame, when checking type 1a and 1b vertical irregularity checks, according to asce7-05, 12.3.2.2, this check is not required for a one-story building, in sdc b,c or d.

The sdc for this frame is D.

My question is, according to asce, is a portal frame considered a one story structure?
 