Hi. I hope you can help me to understand this situation. We have SLD double sectined busbar 110 kV. There is simple SLD below. There is island station 110 kV.
When our object was in project stage, project engineers decided to leave one of Bus Couplers at open position and wrote this information in the project philosophy. I didn't work at this company that time.
Now I have a question, why they did it?
If we close breaker Bus Coupler A2/B2, we will improve stability our system in case when bus B1 fault. Because now, if bus B1 fault, our system will divided into independed systems, and generators which stay on buses A1,A2 can't produce enough power and frequency will decrease.
So I think it will the better way to close Bus Coupler A2/B2.

When our object was in project stage, project engineers decided to leave one of Bus Couplers at open position and wrote this information in the project philosophy. I didn't work at this company that time.
Now I have a question, why they did it?
If we close breaker Bus Coupler A2/B2, we will improve stability our system in case when bus B1 fault. Because now, if bus B1 fault, our system will divided into independed systems, and generators which stay on buses A1,A2 can't produce enough power and frequency will decrease.
So I think it will the better way to close Bus Coupler A2/B2.