Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Do wind turbines using AC/DC/AC topology increase short-circuit power? 1

Status
Not open for further replies.

Bronzeado

Electrical
Jan 6, 2008
272
Dear all,

Do wind turbines using AC/DC/AC topology increase the grid short-circuit power?

Best regards,

Herivelto Bronzeado
 
Replies continue below

Recommended for you

Yeah, but probably a fault current of about 1.2-1.5 per unit. Probably can be ignored for pretty much everything except withstand ratings.
 
Thank you davidbeach,

In this case, could I consider that a wind farm with 50 wind turbines running with this configuration (AC/DC/AC) would increase the short-circuit level by 50x1.2-1.5pu?

We had a problem in a substation busbar (69kV) and we suspect that the wind farm has contribute to the increase of the short-circuit level. But we could not prove that sofar. It is connected 80km away from our substation, being fed by a single line of 69kV.

Do youy think that the influence of that wind farm is considerable?

Regards,

Herivelto
 
You need to contact the turbine/converter manufacturer to determine the actual fault contribution. Then you need to do a proper fault current study to determine the affect at the substation.

Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.
 
Thanks Alan,

The wind farm is embeded in the distribution system and we, as a transmission company, have no contract with them.

My question is a general question as I think that the converter limits (or cut) the current during a short-circuit in the grid.

Best regards,

Herivelto Bronzeado
 
One particular 100 kW model for which I happen to have specs has a fault contribution of 1.0 pu. I don't think it is safe to generalize however.

Alan
“The engineer's first problem in any design situation is to discover what the problem really is.” Unk.
 
What you describe is commonly referred to as a "Type 4" machine. Said machines do not source fault currents past a vendor supplied limit, usually (as David Beach says) somewhere around 1.2 pu.

The last integration study I performed (about two days ago) we were supplied vendor data that showed inverter limits right at 1.2 pu fault current. As a worse case you could assume 1.5 to 2.0 pu fault current, but that really is a poor substitute for the proper information.
 
Thank you all for discussing this matter and thanks Marmite for your valuable link.

Could we conclude that a machine with power electronics coupling does not increase tha shor-circuit level regarding to break current?

In other words, should we be worried about changing our circuit breakers in a substation when a wind farm with electronics coulpling machines is connected to that substation?

Regards,

H. Bronzeado
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor