DirectLogic 5 PLC issue

Status
Not open for further replies.

nornrich

Mechanical
Joined
Jun 12, 2002
Messages
194
Location
US
All,

I have a DL5 Series PLC from Automation direct and I am trying to do a simple motor seal in. I am paralleling the motor contact as a NO contact around the pushbutton input that is triggering the motor to run. For some reason this doesn't seem to seal the motor in. Any thoughts?

Regards,

Rich....

Richard Nornhold, PE
 
Got a drawing?

A couple things come to mind, off hand;

1) Your sealin bit is being used elsewhere too.
2) You're jumping out of the Stage, and resetting it.

Ed
 