I've uploaded a simple SLD to illustrate the fault I'm talking about. Fault is on Feeder A. Fdrs B, C and D contribute currents IB, IC and ID to the fault. This is my first question - the way I see it the cable capacitance has "stored voltage". This tends to support the faulted phase voltage - how exactly I am not sure. Compare this to inductive energy stored in a magnetic field like an induction motor, which discharges current into a fault.
Let's say that the cable capacitance does produce current IB, IC and ID contributions to the fault. I see no need for directional EF protection on these feeders for several reasons.
1) Duration of IB, IC and ID will be typically < 5 cycles.
2) These currents are literally at the threshold of the zero torque line, in fact just outside it as the zero torque line is usually concave. But they could lie just within the operate zone due to resistance resulting in unwanted operation.