I have issue,
2 suppler providing exhaust fan with belt drive motor but the specification say its must be direct drive
and thye tolled me according to big capacity we canot go through direct drive
L/S 7950 SP 550 Pa?
please advise
Option 1: Find a supplier willing to provide what is specified.
Option 2: Request a change order to the specification so that you can provide what is available.
Aside from what the spec says, is there some reason the fan needs to be direct drive? I.E. Space.
If the fan meets all other specified criteria (centrifugal, upblast, inline, etc) and fits in the allocated space, use the belt drive fan.
Is this a roof-mounted fan? Many specs require direct drive because of client desire to eliminate work on the roof, where OSHA has some pretty stiff requirements.