EmergencyPowered
Electrical
- Jul 17, 2005
- 28
Six Generator Detroit Diesel(1750Kva units) 4160vac ASCO system carrying building load varying around 6000Kva. One unit trips 86 lockout from 87 device. Flag on 87 fires so it is not control circuit issue. Will stay on bus at lighter loads but right around this level it trips. Swapped Relay, relay case and reactor unit and it still trips. Put same parts in other generator and they work fine. Testing firm tested all CT's, meggered the cable and local disconnect switch, all good. 3ph Current looks correct on ASCO EDGEWISE meters. Also swapped SR voltage regulator, no change. Rotating rectifier is good. I have HIOKI and a Dranetz Power Analyzer (old monster). Any ideas! I have 3 years of BSEE but didn't finish 4th year. Vectors stuff is not my strong suit. Now I will say "HELP". Uses cross-current CT's on B phase aloso.....