Difference between storm sewer pipe and a culvert pipe

Status
Not open for further replies.

RJSH

Civil/Environmental
Joined
Jan 29, 2013
Messages
39
Location
US
I am trying to understand the difference between storm sewer pipe that is designed by Mannings equation vs culvert design. Why can't we size a culvert using Mannings equation, considering that it is conveying flow from one end to other?
Can someone explain?
 
You can if it acts as an open channel. The complication comes in when either the upstream or downstream end of the culvert is submerged.
 
mannings can be used for calculating normal depth with uniform flow in open channels. culverts rarely flow with a uniform depth, so it really only applies to longer conduits or open channels.

you also need to factor in the tailwater and entrance losses. for a "short" culvert, these are highly critical and may totally override the normal depth. so most culvert capacities are a function of the inlet or outlet conditions.
 
To expand on cvg's point, storm drains are typically hydraulically long; in that they can reach normal depth unless influenced by other controls like tail water. Storm drains also experience inlet & outlet losses which is alluded to by the term "other controls", above.

Culverts are typically short as cvg points out and experience more rapidly changing flow regimes.

Hopes this helps.
 