The simplified Leung method for evaluating the quantity and quality of two phase flow from vessels exposed to external fire gives extremely high values for liquid flow with very small vessels (25-200 litres in our case) and consequently disproprtionately large vent headers. Flowrates calculated indicate that vessels would be emptied in seconds. Our alternative approach of calculating Swelled Volumes, using the equations of M.A.Grolmes, yields results that seem more sensible. Anybody come across a similar situation?
Our approach has been to compare swelled volume with safety factor of 5% added, then to compare this with actual vessel total volume. If the former is less than the latter then it is assumed that there is full liquid droplet disengagement within the vessel. However not withstanding this, the conservative approach is taken of still assuming two phase flow into the vent with 1% v/v liquid. This gives much lower results than Leung.
Our approach has been to compare swelled volume with safety factor of 5% added, then to compare this with actual vessel total volume. If the former is less than the latter then it is assumed that there is full liquid droplet disengagement within the vessel. However not withstanding this, the conservative approach is taken of still assuming two phase flow into the vent with 1% v/v liquid. This gives much lower results than Leung.