I am running through a renovation of a strip mall and have a few questions for clarification:
1. When doing diaphragm design for E/W lateral forces, do I apply load combinations? So that I would really be using either W or 0.7E (equation 16-10 IBC '03)? Obviously for my shear wall I would use combinations, but that's because the D or L from those equations also plays into it. However, for the diaphragm only the lateral load comes into play. I would assume I would have to use the combination because we design all our elements to this.
2. With a flexible diaphragm (only metal deck) if I have one long wall on one side, and 2 walls split by 10' on the other side, I just split the load 50:50 each side and then split the 50% up according to stiffness on the side with 2 walls?
3. As long as wind controls I don't need to design anything for the minimum force for the collector elements in 1605.4.
Thanks in advance.
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke
1. When doing diaphragm design for E/W lateral forces, do I apply load combinations? So that I would really be using either W or 0.7E (equation 16-10 IBC '03)? Obviously for my shear wall I would use combinations, but that's because the D or L from those equations also plays into it. However, for the diaphragm only the lateral load comes into play. I would assume I would have to use the combination because we design all our elements to this.
2. With a flexible diaphragm (only metal deck) if I have one long wall on one side, and 2 walls split by 10' on the other side, I just split the load 50:50 each side and then split the 50% up according to stiffness on the side with 2 walls?
3. As long as wind controls I don't need to design anything for the minimum force for the collector elements in 1605.4.
Thanks in advance.
RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke