Thanks guys – I appreciate the assistance. I just reviewed NFPA 20, Article 6-4.1.2, that states “ ALL Fire Pump motors shall be of the Design Letter B type”. The type that you refer to as “the most commonly used motor”. As a side note, we do not use NEC 2002 nor 1999, but 1996, the Counties that our Permit drawings go through are still all using 1996.
When you refer to the “Locked Rotor Amps” being a function of the HP of the motor, are we saying that if the motor were standing still, that the in-rush current at start up would equal the LRA? Similarly, when the motor reaches the end of its life, (when more current is required to turn it), when it quits, is that stage also equal to LRA? The reason I ask, is that the info that I have traded with other Electrical Designers in the past refers to the saying “the Fire Pump MUST run until it dies”. Therefore, I associate LRA at the end of the life of the motor. If indeed the start up current is equal to LRA, that is why the OCP is sized the way it is, to allow for start up, and motor failure.
Again, thanks for the input, would like to hear your thoughts on the above statement(s), and apologize for my lack of motor knowledge – not one of my strong points!
BB.