I am designing a fall protection system for an existing (1960's) truck loading station at a chemical plant (see attached sketch). A person will be walking ontop of a tanker truck attached to an overhead monorail system. I am designing this for the OSHA 5000# requirement as a static force. Using ASD the existing rafter, bracing, column and anchor bolts are all overstressed.
I feel like I am too conservative on the design approach because the 5000# force is only going to be present for a short time, and after the fall you will just have the weight of the person plus any tools.
Has anyone else been involved with dsigning for fall protection? How have you considered the 5000# load?
I feel like I am too conservative on the design approach because the 5000# force is only going to be present for a short time, and after the fall you will just have the weight of the person plus any tools.
Has anyone else been involved with dsigning for fall protection? How have you considered the 5000# load?