ludwig80
Mechanical
- Dec 29, 2008
- 2
Article 11.1.2 (1) (NFPA-13, ed.2007) can be read as : “ Where areas are not physically separated by a barrier or partition capable of delaying heat from a fire in one area from fusing sprinklers in the adjacent area, the required sprinkler protection for the more demanding design basis shall extend 15 ft (4.6 m) beyond its perimeter. “
Does that barrier need to be fire rated? At first sight, I would say no because NFPA does not mention such thing. But, if the partition is not fire rated, it would mean that it cannot prevent fire entering other room for a certain amount of time.
What do you think? Would a typical gypsum wall arrangement be enough to meet article 11.1.2?
Thank you for your replies.
Does that barrier need to be fire rated? At first sight, I would say no because NFPA does not mention such thing. But, if the partition is not fire rated, it would mean that it cannot prevent fire entering other room for a certain amount of time.
What do you think? Would a typical gypsum wall arrangement be enough to meet article 11.1.2?
Thank you for your replies.