See comments below in **
Suggestions to buzzp (Electrical) May 29, 2002 marked by ///\\The heating affect of DC current vs AC current is compared as follows: The true rms AC current has the same heating affect as the DC current at the same level as the TRMS AC current.
///Please, can you prove it mathematically such that it corresponds to the physical principle/reality of thermal dissipation of heat in the overload or resistor or refer to suitable literature?\\**This has been proven many times. Where do you think TRMS came from? There is no need for me to prove this. If you want, set up an experiment with a resistor and a thermocouple. Measure the heat on the resistor with, say 5 amps DC going through it and then the same thing with 5amp TRMS goiing through it. You will measure the same.
I would think this would be the way to compare the two. Also, you do not want to use an AC overload in a DC application for the following reasons:
1. MFG does not specify this
///At some point in the past, there were no dc overloads however, the dc machines were approximately protected by ac overload. Similar holds true for ac fuses that were used to protect dc loads. Obviously, nowadays things are different.\\2. Device might not monitor DC
///Yes, agree. This would have to be adjusted or customized, which would be approximate as it was done in the past.\\** There is no adjusting an AC device to monitor DC if it was not designed that way. A CT for example will saturate if DC current runs through it and the readings will be meaningless. The only way to interchange an AC monitoring device with DC is to have a shunt, hall-effect sensor, or similar technology.
3. Make and Break ratings of starters (contactors with OL protection built in) has to be higher in DC applications
///This is known fact for all contacts, e.g. relays, contactors, switches, etc.\\** This is why you can NOT use an AC starters in DC applications
4. Arc suppression (no zero cross to quench the arc so other methods are used in switching DC loads)circuitry has to be used (built into DC relays, contactors, starters).
///The dc arc suppression has been around longer than the ac arc suppression at coils, and contacts due to more severe nature of dc arc.\\