we have a data center were the power supplied to the computers is 175 KW.
I calculate the coolig tonnage independently using the following formula:
Tons = GPM X DelatT /24.
where GPM is measured water flow in GPM.
deltaT is (Supply - Return) CHW temp.
This formual produces ~ 40 tons when the numbers are plugged in.
My problem is that the calculated Tons are showing to be ~ 40 tons, when I am expecting 50 tons. The 50 tons is calculated as 175 KW/3.5.
The difference in the tons values I am thinking must be caused by inaccuracy in temp or flow readings.
My question is, am I right to assume that the 175 KW will need at least 50 tons of cooling?.
Thanks