Both York and Trane will provide a factory (only) fast-restart option to the electric centrifs and probably other types. This must be specified in the order as it is not only a controls change, it affects the oil and i think also the refrigerant system designs.
A fast restart will still take around 2-5 mins, versus the 15+ mins of a normal machine, so you need buffer (CHW Storage) or system capacity that can deal with this depending on your intended criticality.
There are often important factory warranty implications when specifying fast restart on chillers. Discuss with your vendor and client and make sure everyone is on board.
The tier level and tonnage of your system would be useful for a more complete answer.