I have a wood pile that was damaged during driving. From what I have been told, the pile split leaving 70% of the bearing surface in tact. During the procedure, we reissued a repair detail for the location that required the addition of 2 piles to compensate for the eccentricity produced by adding only 1 pile. This was 2-1/2 weeks ago.
Now it is time to form the cap and they find out that they only installed one of the two additional piles. Analysis of the group reveals that the piles are severely overstressed. My solution is to add the pile that was missing. The contractor wants to use the damaged pile and avoid driving another pile. Is the acceptance of a “split” wood pile common and something I have been unaware of?
Now it is time to form the cap and they find out that they only installed one of the two additional piles. Analysis of the group reveals that the piles are severely overstressed. My solution is to add the pile that was missing. The contractor wants to use the damaged pile and avoid driving another pile. Is the acceptance of a “split” wood pile common and something I have been unaware of?