I am revisiting some of the grounding techniques we use on CVT circuits.
With respect to the CVT secondary cables... Generally, I would want to ground the cable shield at both ends of the cable (good for high freq. transient suppression). I also know that the bonding conductor connecting the shield to ground should be as short as practically possible. Reducing the length of the bonding conductor will reduce its impedance - an important characteristic when dealing with very high freq. transients (lightning or disconnect switches drawing arcs for example).
So what happens if I want to use two bonding conductors? If these are both now in parallel between the cable shield and ground, the total impedance of the bonding conductors to ground must now be smaller than using just a single conductor. If this is true, could using parallel bonding conductors on cable shields be a means of improving surge suppression?
Thoughts? Comments?
Thanks,
Mark
With respect to the CVT secondary cables... Generally, I would want to ground the cable shield at both ends of the cable (good for high freq. transient suppression). I also know that the bonding conductor connecting the shield to ground should be as short as practically possible. Reducing the length of the bonding conductor will reduce its impedance - an important characteristic when dealing with very high freq. transients (lightning or disconnect switches drawing arcs for example).
So what happens if I want to use two bonding conductors? If these are both now in parallel between the cable shield and ground, the total impedance of the bonding conductors to ground must now be smaller than using just a single conductor. If this is true, could using parallel bonding conductors on cable shields be a means of improving surge suppression?
Thoughts? Comments?
Thanks,
Mark