Recently we had to calculate using IEC 60287 part 2-1 and 1-1 the cable derated ampacity for the following:
3 X (3X630 sqmm) cable, single core, copper conductor, armored, XLPE. (Prysmian) from Transformer (11/0.69 kV) to PC (0,69 kV).
The length is 70 m routed in air, but for 4 m is laid in 3 ducts embedded in concrete (to pass from substation to the transformer ).
Most of IEC is clear and all formula we applied accordingly, but the problem came for T’’’4 (thermal resistance of surrounding medium).
As per IEC-2-1 /2.2.7.3 : “ When the ducts are embedded in concrete, the calculation of the thermal resistance outside the ducts is first of all made assuming a uniform medium outside the ducts having a thermal resistivity equal to the concrete. A correction is then added algebraically to take account of the difference, if any, between the thermal resistivities of concrete and soil for that part of the thermal circuit exterior to the duct bank.”
Correction factor is clear defined, but what about the T4’’’? One could say that this should take the value of concrete thermal resistivity, then calculated correction factor (outside the duct back the filling medium is sand with thermal resistivity of 1,09 km/W) will be added and final result for thermal T’’’4 (total) will be obtained .But is it correct?
The duct bank (750x250 mm) undergorung (-230 mm) has 3 pipes of 225 diameter , wouldn’t be necessary to calculate the mutual heating of the pipe in the middle(the hottest pipe) using IEC 60287-2-1/2.2.3.2 and then to this value should be added the Correction factor?
As a last question, the formula for permissible current rating flowing in one conductor (IEC 60287-1-1/1.4.2.1) has the “n” defined as: number of load-carrying conductors in the cable (conductor of equal size and carrying the same load). Considering that we have 3 single cable in parallel per phase (3 in each pipe X 3 pipes) , what is the correct value for “n” : 1 or 3?
I can send or attach the handmade calculation if any one of you gentlemen would like to help and needs additional information. I mention also that the result obtained considering T4’’’ as rho concrete + correction factor and value of n=1 is 778 A but calculation using ETAP is 403A
Thank you
Florin
Recently we had to calculate using IEC 60287 part 2-1 and 1-1 the cable derated ampacity for the following:
3 X (3X630 sqmm) cable, single core, copper conductor, armored, XLPE. (Prysmian) from Transformer (11/0.69 kV) to PC (0,69 kV).
The length is 70 m routed in air, but for 4 m is laid in 3 ducts embedded in concrete (to pass from substation to the transformer ).
Most of IEC is clear and all formula we applied accordingly, but the problem came for T’’’4 (thermal resistance of surrounding medium).
As per IEC-2-1 /2.2.7.3 : “ When the ducts are embedded in concrete, the calculation of the thermal resistance outside the ducts is first of all made assuming a uniform medium outside the ducts having a thermal resistivity equal to the concrete. A correction is then added algebraically to take account of the difference, if any, between the thermal resistivities of concrete and soil for that part of the thermal circuit exterior to the duct bank.”
Correction factor is clear defined, but what about the T4’’’? One could say that this should take the value of concrete thermal resistivity, then calculated correction factor (outside the duct back the filling medium is sand with thermal resistivity of 1,09 km/W) will be added and final result for thermal T’’’4 (total) will be obtained .But is it correct?
The duct bank (750x250 mm) undergorung (-230 mm) has 3 pipes of 225 diameter , wouldn’t be necessary to calculate the mutual heating of the pipe in the middle(the hottest pipe) using IEC 60287-2-1/2.2.3.2 and then to this value should be added the Correction factor?
As a last question, the formula for permissible current rating flowing in one conductor (IEC 60287-1-1/1.4.2.1) has the “n” defined as: number of load-carrying conductors in the cable (conductor of equal size and carrying the same load). Considering that we have 3 single cable in parallel per phase (3 in each pipe X 3 pipes) , what is the correct value for “n” : 1 or 3?
I can send or attach the handmade calculation if any one of you gentlemen would like to help and needs additional information. I mention also that the result obtained considering T4’’’ as rho concrete + correction factor and value of n=1 is 778 A but calculation using ETAP is 403A