wbd
Electrical
- May 17, 2001
- 659
Hello,
here is my situation: In an old power plant (utility owned), I have buswork that has bolted in Westinghouse DB-50 breakers with LS overcurrent trip devices. The trip device is an air delayed magnetic type of device. On the line side of the breaker, bolted into the busbars feeding the breaker are Shawmut A4BY1600 Class L fuses. This is an installation from the 1950's.
Data:
Available short circuit: 49 kA sym, 66 kA, asym, X/R 6.62
Breaker Ratings: 42 kA sym, 50 kA asym, test X/R 6.6
Fuse Data from let thru table for 50 kA short: Irms 30 kA, Ipeak 68 kA
Without the current limiting fuse in place, the breaker is overdutied. Taking credit for the fuse, the current is reduced to 30 kA, within the rating of the breaker. However, I am not sure about the peak let thru current.
The breaker manual has a note that states the asym interrupting rating is the average rms asym current. With regards to the fuse peak let thru of 68 kA, would that be equivalent to an rms asym current of 48 kA (68 kA/sqrt2)?
Thank you in advance for replies
here is my situation: In an old power plant (utility owned), I have buswork that has bolted in Westinghouse DB-50 breakers with LS overcurrent trip devices. The trip device is an air delayed magnetic type of device. On the line side of the breaker, bolted into the busbars feeding the breaker are Shawmut A4BY1600 Class L fuses. This is an installation from the 1950's.
Data:
Available short circuit: 49 kA sym, 66 kA, asym, X/R 6.62
Breaker Ratings: 42 kA sym, 50 kA asym, test X/R 6.6
Fuse Data from let thru table for 50 kA short: Irms 30 kA, Ipeak 68 kA
Without the current limiting fuse in place, the breaker is overdutied. Taking credit for the fuse, the current is reduced to 30 kA, within the rating of the breaker. However, I am not sure about the peak let thru current.
The breaker manual has a note that states the asym interrupting rating is the average rms asym current. With regards to the fuse peak let thru of 68 kA, would that be equivalent to an rms asym current of 48 kA (68 kA/sqrt2)?
Thank you in advance for replies