Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

CT selection for a generator line

Status
Not open for further replies.

bettoni

Electrical
Joined
Mar 14, 2002
Messages
5
Location
CR
I´m investigating about CT selection, from all the papers about current transformers can´t found any method for TC selection on a generator line. The ANSI/IEEE rules do not apply because of the dc offset of the generator contribution to the fault. My interest is to obtain good measured signals for line relay protection (differential squemes, etc). Please send some information for this case.
 
What is your specific concern?

Is it the measurement of the current during the fault, or the ability of the CT itself to withstand the fault current? I assume since you mention DC offset, you are concerned with the CT saturating during a fault. If you don't think the ANSI/IEEE 'C' class protection rating will work, you may want to check into the IEC or CSA special transient protection class CTs (normally called TPY, TPZ, or TPX). This rating allows one to specify system parameters such as primary time constant, percentage offset of initial peak and then the manufacturer can determine what is called the transient dimensioning factor to drive the CT core design. Normally this is done with gapped core design. In my experience, though it is generally overkill and will cost a good bit extra, but if you think you need it, then...


You may want to contact Ritz, as they make just about any kind of IT to any standard and have pretty good technical folks. Try for starters. I think they have contact info there.
 
All of the generator applications that I have been involved with used standard ANSI Relaying Accuracy CTs. This includes generators up to 900 MVA. The dc offset and possible saturation issues need to be considered, but if applied properly, there should not be a problem.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top