CT REF location

Status
Not open for further replies.

dalas

Electrical
Aug 22, 2005
13
Hi,

i'd like to know

where should i install CT for REF, before (upstream) or after (downstream) 40 Ohm NGR on 150/20 kV 30 MVA Tx ?

thank you





 
Replies continue below

Recommended for you

Do you want the NGR included in or excluded from the zone of the REF?
 
If installed upstream, the CT installation may be subjected to 11,547 volts to ground in the event of a ground fault. Downstream of the resistor the voltage to ground will be zero volts.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Hi.
Standard connection will be upstream ( before NGR) connection of CT.
Biil you are right, in case of "before" is HV type od CT, "after" is low voltage.
Regards.
Slava
 