patm72
Electrical
- Sep 2, 2004
- 42
Can anyone help me shed some light on the following claim found in CSA 22.2 No. 14 (2008) paragraph 4.15.2 regarding MOV's as overvoltage protection devices? Where does it come from?
Surge suppressors of the metal oxide varistor type are not considered to be acceptable overvoltage protection for
equipment and circuits that operate in the primary circuit.
It is found at the bottom of a paragraph about spacing, in fine prints. For the record, a "Primary Circuit" is defined as:
"wiring and components that are conductively connected to the supply circuit".
And a "Secondary circuit" is "wiring and components connected to a circuit, where power is limited by a transformer, rectifier, voltage divider, or similar device that derives power from a primary circuit, and where the short-circuit limit between conductors of the secondary circuit or between conductors and ground is 1500 V•A or less." (so I clearly deal with a Primary circuit).
I was intending to use a MOV type SPD for protecting my electrical equipment (a VFD) from overvoltages. The VFD's could not have these or any other sort of OVP built-in, so now what? The manufacturer "enforces" the use of a choke and EMI filter in front of the VFD to meet CSA 22.2 No. 14 (note that no equivalent of this is applicable in NEC). An EMI filter is quite bulky compared to the SPD's we use all the time.
Thanks.
Surge suppressors of the metal oxide varistor type are not considered to be acceptable overvoltage protection for
equipment and circuits that operate in the primary circuit.
It is found at the bottom of a paragraph about spacing, in fine prints. For the record, a "Primary Circuit" is defined as:
"wiring and components that are conductively connected to the supply circuit".
And a "Secondary circuit" is "wiring and components connected to a circuit, where power is limited by a transformer, rectifier, voltage divider, or similar device that derives power from a primary circuit, and where the short-circuit limit between conductors of the secondary circuit or between conductors and ground is 1500 V•A or less." (so I clearly deal with a Primary circuit).
I was intending to use a MOV type SPD for protecting my electrical equipment (a VFD) from overvoltages. The VFD's could not have these or any other sort of OVP built-in, so now what? The manufacturer "enforces" the use of a choke and EMI filter in front of the VFD to meet CSA 22.2 No. 14 (note that no equivalent of this is applicable in NEC). An EMI filter is quite bulky compared to the SPD's we use all the time.
Thanks.