Have a theory for testing soils in Afghanistan where modern methods and equipment are rare finds. I'm trying to devise a crude substitute method for SPT in order that we can field test compaction, in lieu of proctor/modified proctor. Follow if you will....
SPT is based on 140 lbs @ 30" drop, or 350 ft-lbs. Most hammers are 60%-70%. Found values correlating to 60%.
VL Very Loose
L Loose
M Medium
D Dense
VD Very Dense
From Skempton 1986
VL L M D VD
Dr (%)------------0 15 35 65 85 100
SPT [N60] 0 3 8 25 42 58
Of course, we don't have SPT rigs here, so I propose:
1) 20 LB sledgehammer
2) person shoulder height 60"
3) drop from 36" above shoulder height
4) 2.5" std pipe 36" above ground
5) flat plate on pipe edge
6) 90% energy efficiency
7) reduce drive distance
8) no boring samples are taken
Energy = F*d
F, one drop, = 60%(350)(12/[N60])
E = 0.9*20*(60+36-36)/12 = 90 lbft
VL L M D VD
Dr (%)------------0 15 35 65 85 100
SPT (N60) 0 3 8 25 42 58
F (lbs)-----------0 630 1680 5250 8820 12180
E (lbft, prop'd)--90 90 90 90 90 90
'd' (in/blow)-----0 1.71 0.64 0.21 0.12 0.089
N per 1"----------0 0.85 1.56 4.76 8.33 11.2
N per 2"----------0 1.17 3.13 9.52 16.7 22.5
N per 4"----------0 2.34 6.25 19.0 33.3 44.9
Rounded N/4-------0 3 7 19 34 45
In lieu of having "expensive" lab tests done, this is my proposal. [Remember, this is AFG we're talking about.]
After each layer is compacted, the Contractor while being observed by COR & CI perform these tests in random spots, will set up the pipe and drive the pipe 2" into the ground. Then the he would drive the pipe another 2" into the ground and record the number of blows. Then he would drive the pipe another 2" into the ground and record the number of blows.
The last two blow counts are what we would measure (N per 4"). The goal would be that the Contractor keeps making passes until each layer of fill achieves an "N" of 34.
I know some poor soul will suffer swinging a hammer "exactly" the same way every time, but what do you think?
v/r,
Jacob Parker, PE
TF Mountain Warrior
FOB Fenty
Afganistan
SPT is based on 140 lbs @ 30" drop, or 350 ft-lbs. Most hammers are 60%-70%. Found values correlating to 60%.
VL Very Loose
L Loose
M Medium
D Dense
VD Very Dense
From Skempton 1986
VL L M D VD
Dr (%)------------0 15 35 65 85 100
SPT [N60] 0 3 8 25 42 58
Of course, we don't have SPT rigs here, so I propose:
1) 20 LB sledgehammer
2) person shoulder height 60"
3) drop from 36" above shoulder height
4) 2.5" std pipe 36" above ground
5) flat plate on pipe edge
6) 90% energy efficiency
7) reduce drive distance
8) no boring samples are taken
Energy = F*d
F, one drop, = 60%(350)(12/[N60])
E = 0.9*20*(60+36-36)/12 = 90 lbft
VL L M D VD
Dr (%)------------0 15 35 65 85 100
SPT (N60) 0 3 8 25 42 58
F (lbs)-----------0 630 1680 5250 8820 12180
E (lbft, prop'd)--90 90 90 90 90 90
'd' (in/blow)-----0 1.71 0.64 0.21 0.12 0.089
N per 1"----------0 0.85 1.56 4.76 8.33 11.2
N per 2"----------0 1.17 3.13 9.52 16.7 22.5
N per 4"----------0 2.34 6.25 19.0 33.3 44.9
Rounded N/4-------0 3 7 19 34 45
In lieu of having "expensive" lab tests done, this is my proposal. [Remember, this is AFG we're talking about.]
After each layer is compacted, the Contractor while being observed by COR & CI perform these tests in random spots, will set up the pipe and drive the pipe 2" into the ground. Then the he would drive the pipe another 2" into the ground and record the number of blows. Then he would drive the pipe another 2" into the ground and record the number of blows.
The last two blow counts are what we would measure (N per 4"). The goal would be that the Contractor keeps making passes until each layer of fill achieves an "N" of 34.
I know some poor soul will suffer swinging a hammer "exactly" the same way every time, but what do you think?
v/r,
Jacob Parker, PE
TF Mountain Warrior
FOB Fenty
Afganistan