Crane Beam Deflection 3

Status
Not open for further replies.

dik

Structural
Apr 13, 2001
26,097
Is there a code related article for crane beam deflection? I've usually used L/480 or 1/2" maximum. I was wondering if this was quantified, somewhere. Thanks in advance.

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
Replies continue below

Recommended for you

From Chapter 14 of AISC DG 7:

Screenshot_2021-05-11_110656_cf6sor.png
 
Thanks, Gentlemen... I'll bump it up a tad... still keeping the 1/2"

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
Hi dik

You’re welcome

“Do not worry about your problems with mathematics, I assure you mine are far greater.” Albert Einstein
 
Eurocodes have two parts dedicated to cranes.
One to quantify the loads, one for the design of the crane beams.
EN 1991-3
EN 1993-6
Have also a look at ISO/DIS 11660-6

From the top of my head, crane girders are limited to L/600 and 25 mm vertical deflection.
Lateral also L/600.
 
Thanks... got it fixed.

image_bvdjuq.png


Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
^^^ I wouldn't know, but I'd start my search on zlibrary (z-lib.org => books) ... Has many other interesting documents as well (don't type "structural" in the search box or you're gone for hours...)
 