Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Covered Patio

Status
Not open for further replies.

sfallows

Specifier/Regulator
Joined
Oct 18, 2007
Messages
45
Location
US
I was wondering about Covered patios. I have been looking into the requirements about when they are required. I hear this both ways about when they are or are not required, and I can't find anything in NFPA 13. Am I just missing it?
 
Do not have the book with me

Look under canopy or overhang

Normaly anything over 4 feet with some exceptions
 
Take a look at NFPA 13 2010 8.15.7, beginning to end. Should answer all your questions.
 
If you are dealing with Group R-2 apartments of combustible construction, the 2009 International Fire Code has sprinkler protection requirements that are more restrictive than NFPA 13 for balconies and decks.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top