Four years ago we put in a painted, galvanized fire sprinkler system in an animal rendering plant. At the time the system was installed we had no idea how wet and corrosive of an environment we were working with.
Now the pipe is falling apart at the fittings and the white nylon coated heads have turned black.
NFPA 13.A.8.16.4.2.1 states, "Types of locations where corrosive conditions can exist include bleacheries, dye houses, metal plating prosesses, animal pens and certain chemical plants.
If corrosive conditions are not of great intensity and humidity is not abnormally high, good results can be obtained by a protective coating of red lead and varnish or by a good grade of commercial acid-resisting paint. The paint manufacturer's instructions should be followed in the preparation of the surface and in the method of application.
Where moisture conditions are severe but corrosive conditions are not of great intensity, copper tube or galvanized pipe, fittings and hangers might be suitable. The exposed threads of steel pipe should be painted.
In instances where the piping is not readily accessable and where the exposure to corrosive fumes is severe. either a protective coating of high quality can be employed or some form of corrosion-resistant material used."
We've talked about using stainless pipe to replace the system but we're not even sure how long the stainless steel would last given the high moisture levels and the corrosive fumes we've got floating around here.
We've tossed around a lot of ideas but none of which I'm comfortable using at this point.
Have any of you dealt with a problem like this and if so, what was your solution?
Thanks.
Now the pipe is falling apart at the fittings and the white nylon coated heads have turned black.
NFPA 13.A.8.16.4.2.1 states, "Types of locations where corrosive conditions can exist include bleacheries, dye houses, metal plating prosesses, animal pens and certain chemical plants.
If corrosive conditions are not of great intensity and humidity is not abnormally high, good results can be obtained by a protective coating of red lead and varnish or by a good grade of commercial acid-resisting paint. The paint manufacturer's instructions should be followed in the preparation of the surface and in the method of application.
Where moisture conditions are severe but corrosive conditions are not of great intensity, copper tube or galvanized pipe, fittings and hangers might be suitable. The exposed threads of steel pipe should be painted.
In instances where the piping is not readily accessable and where the exposure to corrosive fumes is severe. either a protective coating of high quality can be employed or some form of corrosion-resistant material used."
We've talked about using stainless pipe to replace the system but we're not even sure how long the stainless steel would last given the high moisture levels and the corrosive fumes we've got floating around here.
We've tossed around a lot of ideas but none of which I'm comfortable using at this point.
Have any of you dealt with a problem like this and if so, what was your solution?
Thanks.