May 24, 2012 #1 RamiA Mechanical Joined May 24, 2012 Messages 1 Location US I am trying to calculate NPSHA on cooling tower pumps we have on-site to check if they meet the mfg NPSHR and I was wondering if I should treat it as an open tank and add atmospheric head on it.
I am trying to calculate NPSHA on cooling tower pumps we have on-site to check if they meet the mfg NPSHR and I was wondering if I should treat it as an open tank and add atmospheric head on it.
May 24, 2012 #2 JJPellin Mechanical Joined Oct 29, 2002 Messages 2,195 Location US Yes. Johnny Pellin Upvote 0 Downvote
May 24, 2012 #3 bimr Civil/Environmental Joined Feb 25, 2003 Messages 9,388 Location US The cooling tower basin is not any different than any other water tank. Add the atmospheric head on to the level of the cooling tower basin. Upvote 0 Downvote
The cooling tower basin is not any different than any other water tank. Add the atmospheric head on to the level of the cooling tower basin.