- Mar 19, 2009
- 15
I've got a problem with a cooling tower. The cooling tower is cooling service water that is basically city water with the normal, small concentrations of biocide and dispersants which are added and monitored by the water chemical company. The tower is performing well thermally, but has failed the "drift" test - drift being the very small amount of mist carryover that results from the gas-liquid contact. The guarantee is 0.0005%, and the drift is being measured at 0.001%. The manufacturer is pointing to the water and is saying there must be some contaminant or chemical that is skewing the droplet distribution from the spray nozzles towards small droplet sizes. The small droplet sizes are then defeating the chevron style mist eliminators because they don't have enough mass for an inertial impaction type of mist eliminator and are following the air through. I am having a hard time visualizing how the small amount of water treatment chemicals could have a significant impact on droplet size distribution. I am used to thinking in terms of hydraulic pressure and design of single-fluid nozzles as the primary factors affecting droplet size. In any event, we are testing the water for chemical concentrations. The surface tension comes in close to water - which should be OK. What else should I be looking for as a cause of the excess drift? Overloading and flooding the mist eliminators? Anything else?