control valves versus self acting regulators 1

Status
Not open for further replies.

Refining1

Petroleum
Joined
Apr 14, 2007
Messages
2
Location
GB
Hi, While sizing and selecting a control valve I understand that the term Cv is used and this is calculated using ISA 75.01 standard for valve sizing.However for a regulator there are no such standards and capacity of a regulator is determined from the flow rates published at certain droop. If both regulators and valves are used on similar applications then why two different sizing methodology? Any thoughts
 
A control valve does not include any controller. Cv is the information one needs in order to select a control valve. A regulator has an integral controller which is what causes droop. Droop is the information that one needs to select a regulator.
 
A proprotional controller introduces droop; an integral controller eliminates it. Most mechanical regulators don't have an integrating elelment.
 