cssvas, You've made a major capital investment in a high tech/high performance control instrument, that has been specially designed by a CV maufacturer. Why would you want to install it backwards and waste that investment? If this is a field problem and wasn't caught in the instrument ring-out, I hope the control set was set up in a standard ISA control valve station set-up. If so, open the by-pass close the blocks, bleed it off and rotate the valve so that the flow is entering the inlet flange.
If the above isn't do-able, contact the Manu'f. for the tech data on reverse flow through the valve, if they have it. They will in all probability tell you to reverse the valve.
Godluck.
saxon