Control Logix CPU to control remote Siemens I/O S5-S7

Status
Not open for further replies.

panou

Electrical
Apr 21, 2005
33
Good morning
Is it possible to have a central rack with 1756-L55 CLX controlller and connect this via network with remote I/O of Siemens type S5 and S7 in order to control and monitor this equipment? What are the things should i consider : new hardware, new software etc.
 
Replies continue below

Recommended for you

Hello;
If the Siemens RIO has a Profibus interface (most S7 does) then yes. You will need a SST/Woodhead SST-CLX-PFB card.
 