I have been catching grief for having threaded connections on bulk liquid tanks. The knock on them is that they can easily be broken (with which I agree), and that the breach will be difficult to remediate if a break occurs (which I consider less valid).
In my mind, the breakage risk is more a function of size (and the connections in question ARE small, 3/4" and 1"), than of joining technology. A flanged nozzle in this range is just as easily broken as a threaded fitting. Also, a broken fitting on a filled liquid tank is a challenge to repair in any case; what makes the difference if it is threaded or flanged?
Avoiding small connections will be difficult. The half couplings are meant to accept thermowells, pressure transmitters, and ball valves for sampling. All of these have inherently small process connections. In addition, half couplings are nice because they are short, making the shipping envelope smaller (most of my tanks are shop-fabbed), and allowing a little better penetration by thermowells and other devices.
I am considering ignoring the concern about threaded connections, and adopting a minimum pipe size to mitigate the breakage risk. Even then, many devices (sensors, transmitters) will neck down from the process connection, merely displacing the weak point. Perhaps there are governing codes, of which I am unaware. What is considered best practice?
In my mind, the breakage risk is more a function of size (and the connections in question ARE small, 3/4" and 1"), than of joining technology. A flanged nozzle in this range is just as easily broken as a threaded fitting. Also, a broken fitting on a filled liquid tank is a challenge to repair in any case; what makes the difference if it is threaded or flanged?
Avoiding small connections will be difficult. The half couplings are meant to accept thermowells, pressure transmitters, and ball valves for sampling. All of these have inherently small process connections. In addition, half couplings are nice because they are short, making the shipping envelope smaller (most of my tanks are shop-fabbed), and allowing a little better penetration by thermowells and other devices.
I am considering ignoring the concern about threaded connections, and adopting a minimum pipe size to mitigate the breakage risk. Even then, many devices (sensors, transmitters) will neck down from the process connection, merely displacing the weak point. Perhaps there are governing codes, of which I am unaware. What is considered best practice?