Connection experts: I need some critical feedback on a special connection.
The attached pdf is a 90%.
1. Existing bridge sidewalk is 12" thick at tip.
2. New 16" ductile iron pipe, supported at 9' oc. 166 plf, plus seismic for SDS = 1.0. moment, shear, and axial is a little complicated, but the governing action is moment.
Mu = factored moment = 50 k-in.
3. The continuous #4 bar (probably Fy=40ksi since constructed circa 1965) and the perpendicular hooked top bars #4 @18" certainly provide strength and confinement, but may not be sufficient.
4. The limit states are easy for steel and bolts, except I'm not sure how to analyze concrete breakout at the top upper right corner. That is, the (3) bolts in shear that tend to break out the top corner - or at least cause linear cracking.