Jun 17, 2016 #1 Weldinspect Mechanical Joined Feb 13, 2010 Messages 211 Location SV What do you people advise for pipe valves insulation to prevent condensation? http://albanesmolina.wix.com/home
What do you people advise for pipe valves insulation to prevent condensation? http://albanesmolina.wix.com/home
Jun 17, 2016 #2 dbill74 Mechanical Joined Feb 26, 2009 Messages 538 Location US Anywhere from 2-4 inches. It depends on the temperature of the fluid in the pipe and temperature of the space the pipe is located in. For valves, should be at least as thick as the insulation for the piping. Upvote 0 Downvote
Anywhere from 2-4 inches. It depends on the temperature of the fluid in the pipe and temperature of the space the pipe is located in. For valves, should be at least as thick as the insulation for the piping.