cal91
Structural
- Apr 18, 2016
- 294
I have an old concrete building, 6" concrete walls X 25'-0" high. They run about 1'-9" into the ground, but have no footing.
There are 18" X 18" Pilasters every 20'-0", supported by a 3' X 3' footing.
Contractor is adding a second floor inside the building, supported by new walls just inside the 6" concrete exterior walls. He wants to know if we can use these walls for shear so we don't have to make the new walls shear walls.
The minimal footing scares me. Just the weight of the wall tributary to a 3X3 footing is 37.5 kips. Assuming the footing supports the wall thats 4200 psi. Or 3750 psi assuming the wall bears all of it's own weight directly to the soil.
There's not even a geotechnical report, so I can't justify using more than 1500 psf...
Not sure I even feel comfortable doing anything to this building even if I'm staying away from the walls. Any thoughts or suggestions?