For a standard concrete mix made with 40 mm coarse aggregate, 25 MPa, southern Ontario aggrgates, high range water reducer, what shrinkage strain range should be expected? I am told 0.05% to 0.07% by a concrete supplier, but for a concrete with 40 mm aggregate that seems to me to be rather high, particularly if it is at the 0.07% end of the range. That is what I would have thought would be the case with 20 mm coarse aggregate.
Any comment?
I am well aware that lower shrinakge concrete (less than or equal to 0.04% as specified in CSA A23.1) can be achieved, and have successfully used it on a number of projects, but that comes at a premium cost to "standard" mixes and is meeting some resistance from our client.
Any comment?