I have a concrete retaining wall that is retaining approximately 15FT. See attached. An exterior building wall for a (1)-story wood-framed commercial building will be built on top of this retaining wall.
I designed this wall for at-rest pressure (62H per the geotech report). Here are my questions:
1) The geotech report says, "It is important that below-grade building walls that generally are designed for minimal displacements at the top of the wall should not be backfilled until the walls are adequately braced by permanent structural framing." So, obviously this isn't an option for me because we need to backfill the wall in order to place the slab on grade. I understand that you can shore the wall while it is being backfilled, however our office policy is to just design the wall for the at-rest pressures and figure that doing so will prevent us from having to shore the wall. Does anyone disagree with this logic?
2) I used a surcharge load of 250 PSF over the heel. To me, this 250 psf represents the backfilling and compacting. The actual first floor occupancy live load is 100 psf and we have a 4" slab on grade (so 50 PSF dead load). I'm not sure if it is appropriate to use 250 psf for backfilling/compacting. I think this is standard practice in our office. I would like to just use the 150 psf occupancy load for the surcharge load. Thoughts?
I designed this wall for at-rest pressure (62H per the geotech report). Here are my questions:
1) The geotech report says, "It is important that below-grade building walls that generally are designed for minimal displacements at the top of the wall should not be backfilled until the walls are adequately braced by permanent structural framing." So, obviously this isn't an option for me because we need to backfill the wall in order to place the slab on grade. I understand that you can shore the wall while it is being backfilled, however our office policy is to just design the wall for the at-rest pressures and figure that doing so will prevent us from having to shore the wall. Does anyone disagree with this logic?
2) I used a surcharge load of 250 PSF over the heel. To me, this 250 psf represents the backfilling and compacting. The actual first floor occupancy live load is 100 psf and we have a 4" slab on grade (so 50 PSF dead load). I'm not sure if it is appropriate to use 250 psf for backfilling/compacting. I think this is standard practice in our office. I would like to just use the 150 psf occupancy load for the surcharge load. Thoughts?